Cyber Power Systems - CP850PFCLCD - Working

What UPS Brand Do You Use?


  • Total voters
    34
Status
Not open for further replies.

Yatti420

Wizard
Joined
Aug 12, 2012
Messages
1,437
Just wanted to confirm the pure sine wave series from Cyber Power seems to be working no problem with NUT.. Cyber Power Systems - CP850PFCLCD - Working with usbhid-ups

See ya,

Code:
[root@NAS] ~# upsc ups
battery.charge: 100
battery.charge.low: 10
battery.charge.warning: 20
battery.mfr.date: CPS
battery.runtime: 2580
battery.runtime.low: 300
battery.type: PbAcid
battery.voltage: 16.0
battery.voltage.nominal: 24
device.mfr: CP850PFCLCD
device.model: CRDA103*AF1
device.serial: CPS
device.type: ups
driver.name: usbhid-ups
driver.parameter.pollfreq: 30
driver.parameter.pollinterval: 2
driver.parameter.port: /dev/ugen1.3
driver.version: 2.7.1
driver.version.data: CyberPower HID 0.3
driver.version.internal: 0.38
input.transfer.high: 139
input.transfer.low: 88
input.voltage: 122.0
input.voltage.nominal: 120
output.voltage: 138.0
ups.beeper.status: enabled
ups.delay.shutdown: 20
ups.delay.start: 30
ups.load: 14
ups.mfr: CP850PFCLCD
ups.model: CRDA103*AF1
ups.productid: 0501
ups.realpower.nominal: 510
ups.serial: CPS
ups.status: OL
ups.test.result: No test initiated
ups.timer.shutdown: -60
ups.timer.start: -60
ups.vendorid: 0764
 

Yatti420

Wizard
Joined
Aug 12, 2012
Messages
1,437
With Overrides..

Code:
[root@NAS] ~# upsc ups
battery.charge: 100
battery.charge.low: 10
battery.charge.warning: 20
battery.mfr.date: CPS
battery.runtime: 2910
battery.runtime.low: 300
battery.type: PbAcid
battery.voltage: 12
battery.voltage.nominal: 12
device.mfr: CP850PFCLCD
device.model: CRDA103*AF1
device.serial: CPS
device.type: ups
driver.name: usbhid-ups
driver.parameter.pollfreq: 30
driver.parameter.pollinterval: 2
driver.parameter.port: /dev/ugen1.3
driver.version: 2.7.1
driver.version.data: CyberPower HID 0.3
driver.version.internal: 0.38
input.transfer.high: 139
input.transfer.low: 88
input.voltage: 121.0
input.voltage.nominal: 120
output.voltage: 137.0
ups.beeper.status: enabled
ups.delay.shutdown: 20
ups.delay.start: 30
ups.load: 13
ups.mfr: CP850PFCLCD
ups.model: CRDA103*AF1
ups.productid: 0501
ups.realpower.nominal: 510
ups.serial: CPS
ups.status: OL
ups.test.result: No test initiated
ups.timer.shutdown: -60
ups.timer.start: -60
ups.vendorid: 0764


Code:
[root@NAS] ~# upscmd -l ups
Instant commands supported on UPS [ups]:
 
beeper.disable - Disable the UPS beeper
beeper.enable - Enable the UPS beeper
beeper.mute - Temporarily mute the UPS beeper
beeper.off - Obsolete (use beeper.disable or beeper.mute)
beeper.on - Obsolete (use beeper.enable)
load.off - Turn off the load immediately
load.off.delay - Turn off the load with a delay (seconds)
load.on - Turn on the load immediately
load.on.delay - Turn on the load with a delay (seconds)
shutdown.return - Turn off the load and return when power is back
shutdown.stayoff - Turn off the load and remain off
shutdown.stop - Stop a shutdown in progress
test.battery.start.deep - Start a deep battery test
test.battery.start.quick - Start a quick battery test
test.battery.stop - Stop the battery test
top - Stop the battery test
 

Attachments

  • new.png
    new.png
    51.6 KB · Views: 543

Yatti420

Wizard
Joined
Aug 12, 2012
Messages
1,437
Just wanted to confirm the pure sine wave series from Cyber Power seems to be working no problem with NUT.. Cyber Power Systems - CP850PFCLCD - Working with usbhid-ups

See ya,

Code:
[root@NAS] ~# upsc ups
battery.charge: 100
battery.charge.low: 10
battery.charge.warning: 20
battery.mfr.date: CPS
battery.runtime: 2580
battery.runtime.low: 300
battery.type: PbAcid
battery.voltage: 12
battery.voltage.nominal: 12
device.mfr: CP850PFCLCD
device.model: CRDA103*AF1
device.serial: CPS
device.type: ups
driver.name: usbhid-ups
driver.parameter.pollfreq: 30
driver.parameter.pollinterval: 2
driver.parameter.port: /dev/ugen1.3
driver.version: 2.7.1
driver.version.data: CyberPower HID 0.3
driver.version.internal: 0.38
input.transfer.high: 139
input.transfer.low: 88
input.voltage: 122.0
input.voltage.nominal: 120
output.voltage: 138.0
ups.beeper.status: enabled
ups.delay.shutdown: 20
ups.delay.start: 30
ups.load: 14
ups.mfr: CP850PFCLCD
ups.model: CRDA103*AF1
ups.productid: 0501
ups.realpower.nominal: 510
ups.serial: CPS
ups.status: OL
ups.test.result: No test initiated
ups.timer.shutdown: -60
ups.timer.start: -60
ups.vendorid: 0764


Code:
[root@NAS] ~# upscmd -l ups
Instant commands supported on UPS [ups]:
 
beeper.disable - Disable the UPS beeper
beeper.enable - Enable the UPS beeper
beeper.mute - Temporarily mute the UPS beeper
beeper.off - Obsolete (use beeper.disable or beeper.mute)
beeper.on - Obsolete (use beeper.enable)
load.off - Turn off the load immediately  ** (Immediate Power Off - Don't Run This))
load.off.delay - Turn off the load with a delay (seconds) ** (Immediate Power Off - Don't Run This))
load.on - Turn on the load immediately
load.on.delay - Turn on the load with a delay (seconds)
shutdown.return - Turn off the load and return when power is back
shutdown.stayoff - Turn off the load and remain off
shutdown.stop - Stop a shutdown in progress
test.battery.start.deep - Start a deep battery test
test.battery.start.quick - Start a quick battery test
test.battery.stop - Stop the battery test
 

Attachments

  • new.png
    new.png
    51.6 KB · Views: 450

scurrier

Patron
Joined
Jan 2, 2014
Messages
297
No one's replied yet so I just wanted to thank you for posting this since I'll be in the market for a UPS soon.
 

Yatti420

Wizard
Joined
Aug 12, 2012
Messages
1,437
Just remember to choose the cpcf1000pfclcd usbhid driver and all should work well.. This is most basic.. Single UPS wired with USB..
 

SweetAndLow

Sweet'NASty
Joined
Nov 6, 2013
Messages
6,421
just bought the cp1000pfclcd and i'm glad to see this thread showing it working.
 

Yatti420

Wizard
Joined
Aug 12, 2012
Messages
1,437
Not a problem.. How much wattage you using.. What is your expected run time with the 1000VA?

Also I'm curious what sensitivity level people are choosing.. I know low isn't recommended for electronics I believe.. See Input Transfer..

Code:
input.transfer.high: 139
input.transfer.low: 88
input.voltage: 122.0
input.voltage.nominal: 120
 

desiguy

Cadet
Joined
Feb 12, 2014
Messages
8
thanks for the heads up. I am going to be picking up a cyberpower cp850pfclcd in the next couple of weeks.
 

Radu

Dabbler
Joined
Mar 7, 2014
Messages
45
Arrghhh i can not find it in my country :(
 

SweetAndLow

Sweet'NASty
Joined
Nov 6, 2013
Messages
6,421
So I'm using 48watts. Not sure of expected runtime yet i need to let it charge fully.

I'm not sure if it is working though. /var/log/messages seems to report strange things at start up. after it was all said and done there is a pid file.
Code:
Mar 12 12:26:22 FreeNAS notifier: nut not running? (check /var/db/nut/upsd.pid).
Mar 12 12:26:22 FreeNAS notifier: nut_upsmon not running? (check /var/db/nut/upsmon.pid).
Mar 12 12:26:22 FreeNAS notifier: nut_upslog not running? (check /var/db/nut/upslog.pid).
Mar 12 12:26:22 FreeNAS notifier: Will not 'restart' nut because nut_enable is NO.
Mar 12 12:26:22 FreeNAS notifier: Will not 'restart' nut_upsmon because nut_upsmon_enable is NO.
Mar 12 12:26:22 FreeNAS notifier: Will not 'restart' nut_upslog because nut_upslog_enable is NO. Mar 12 12:26:26 FreeNAS manage.py: [common.pipesubr:57] Popen()ing: /usr/local/bin/warden list -v
Mar 12 12:26:26 FreeNAS last message repeated 2 times
Mar 12 12:26:52 FreeNAS notifier: nut not running? (check /var/db/nut/upsd.pid).
Mar 12 12:26:52 FreeNAS notifier: nut_upsmon not running? (check /var/db/nut/upsmon.pid).
Mar 12 12:26:52 FreeNAS notifier: nut_upslog not running? (check /var/db/nut/upslog.pid).
Mar 12 12:26:52 FreeNAS notifier: nut not running? (check /var/db/nut/upsd.pid).
Mar 12 12:26:56 FreeNAS notifier: Using subdriver: CyberPower HID 0.3 Mar 12 12:26:56 FreeNAS notifier: Network UPS Tools - Generic HID driver 0.37 (2.6.5) Mar 12 12:26:56 FreeNAS notifier: USB communication driver 0.31 Mar 12 12:27:00 FreeNAS notifier: Network UPS Tools - UPS driver controller 2.6.5
Mar 12 12:27:00 FreeNAS notifier: Starting nut.
Mar 12 12:27:00 FreeNAS notifier: fopen /var/db/nut/upsd.pid: No such file or directory Mar 12 12:27:00 FreeNAS notifier: listening on 127.0.0.1 port 3493 Mar 12 12:27:00 FreeNAS notifier: Connected to UPS [ups]: usbhid-ups-ups
Mar 12 12:27:00 FreeNAS notifier: nut_upsmon not running? (check /var/db/nut/upsmon.pid). Mar 12 12:27:00 FreeNAS notifier: Starting nut_upsmon.
Mar 12 12:27:00 FreeNAS notifier: fopen /var/db/nut/upsmon.pid: No such file or directory
Mar 12 12:27:00 FreeNAS notifier: UPS: ups (master) (power value 1)
Mar 12 12:27:00 FreeNAS notifier: nut_upslog not running? (check /var/db/nut/upslog.pid). Mar 12 12:27:00 FreeNAS notifier: Starting nut_upslog.
 

Yatti420

Wizard
Joined
Aug 12, 2012
Messages
1,437
You should let it charge fully before using it.. I get 49-50 minutes estimated by the UPS.
 

SweetAndLow

Sweet'NASty
Joined
Nov 6, 2013
Messages
6,421
You should let it charge fully before using it.. I get 49-50 minutes estimated by the UPS.
Hmmm... Didn't see that called out anywhere in the directions. It said it won't fully work until charged but not to use it before fully charged.
 

Yatti420

Wizard
Joined
Aug 12, 2012
Messages
1,437
I haven't actually tested the run-time in real life.. You could probably do this in command line ssh.. I know the "Long/short" tests works..
 

SweetAndLow

Sweet'NASty
Joined
Nov 6, 2013
Messages
6,421
You should let it charge fully before using it.. I get 49-50 minutes estimated by the UPS.

At ~50 watt usage i get a runtime of 60min.
 

SweetAndLow

Sweet'NASty
Joined
Nov 6, 2013
Messages
6,421
Yatti420:
I notice you are using 2.7.1 driver how did you get this driver? What version of freenas are you running? I have version 2.6.5 and am seeing connection lost errors and "Data for UPS is stale - check driver" errors
 

clicq

Dabbler
Joined
Jan 3, 2014
Messages
17
Yatti420:
I notice you are using 2.7.1 driver how did you get this driver? What version of freenas are you running? I have version 2.6.5 and am seeing connection lost errors and "Data for UPS is stale - check driver" errors


NUT 2.7.1 is included in the latest FreeNAS release (I'm using 9.2.1.2, I'm not sure when it was updated).

I'm still seeing the same "Data is stale" errors as before, and I have the CP1000PFCLCD.
 

Yatti420

Wizard
Joined
Aug 12, 2012
Messages
1,437
what if you cycle the UPS service with everything disconnected and then try again etc.. Does it clear out the stale data? Could it be bad USB cable?
 

clicq

Dabbler
Joined
Jan 3, 2014
Messages
17
what if you cycle the UPS service with everything disconnected and then try again etc.. Does it clear out the stale data? Could it be bad USB cable?


It's an intermittent failure, and it fixes itself usually in the next second or two. Here's a snippet from my log:

Mar 15 12:01:08 ama upsd[9050]: Data for UPS [ups] is stale - check driver
Mar 15 12:01:08 ama upsd[9050]: UPS [ups] data is no longer stale
Mar 15 12:09:08 ama upsd[9050]: Data for UPS [ups] is stale - check driver
Mar 15 12:09:08 ama upsd[9050]: UPS [ups] data is no longer stale
Mar 15 13:10:26 ama upsd[9050]: Data for UPS [ups] is stale - check driver
Mar 15 13:10:28 ama upsd[9050]: UPS [ups] data is no longer stale

I haven't tried another USB cable, but it's worth a shot if I can find a spare -- I'll try it and update.

So you're not seeing any of these sorts of errors?
 

Yatti420

Wizard
Joined
Aug 12, 2012
Messages
1,437
To confirm this is the 1000VA versus the 850VA correct? This would be in the messages log?
 