LOWBATT - ups email sent, but UPS at full charge?

Status
Not open for further replies.

Francis Reader

Dabbler
Joined
Mar 18, 2015
Messages
19
output from upsc ups@localhost below.

I'm getting regular (every couple of days), emails sent reporting LOWBATT but upon inspection, the UPS is fine.

I've tested the UPS and reporting, (plugged freenas into live mains, and drew down the UPS battery to test the shutdown was working.)

Ideas?

-=----
battery.charge: 100
battery.charge.low: 10
battery.charge.warning: 20
battery.mfr.date: CPS
battery.runtime: 930
battery.runtime.low: 300
battery.type: PbAcid
battery.voltage: 14.1
battery.voltage.nominal: 12
device.mfr: CPS
device.model: CP 1350C
device.type: ups
driver.name: usbhid-ups
driver.parameter.pollfreq: 30
driver.parameter.pollinterval: 2
driver.parameter.port: auto
driver.version: 2.7.2
driver.version.data: CyberPower HID 0.3
driver.version.internal: 0.38
input.transfer.high: 140
input.transfer.low: 90
input.voltage: 121.0
input.voltage.nominal: 120
output.voltage: 121.0
ups.beeper.status: enabled
ups.delay.shutdown: 20
ups.delay.start: 30
ups.load: 39
ups.mfr: CPS
ups.model: CP 1350C
ups.productid: 0501
ups.realpower.nominal: 298
ups.status: OL
ups.test.result: Done and passed
ups.timer.shutdown: -60
ups.timer.start: 0
ups.vendorid: 0764
 

SavageCore

Dabbler
Joined
Jun 24, 2015
Messages
17
I get the same since upping the load. I have my NAS, 4 port switch, router, modem and gaming PC all connected now. Gone from drawing 50 or so watts to 200-480w. Max of the UPS is 540, need another really for PC but we have some wiring issues we're trying to pinpoint in the house so power is dodgy..

So is it incorrectly sending LOWBATT when really it's some sort of near max load error? I get them when playing a game or otherwise causing high load. When both the NAS and gaming system are idle all is well.

Sorry to dig up old post, found this from search.
 
Last edited:

jde

Explorer
Joined
Aug 1, 2015
Messages
93
what brand/model is the UPS? How old is the UPS? Perhaps the battery is slowly flaking out. Maybe try putting a steady, relatively known load on the UPS and see how long it runs on the battery. If it runs out of juice earlier than expected try replacing the battery.
 

SavageCore

Dabbler
Joined
Jun 24, 2015
Messages
17
In my signature, CyberPower CP900EPFCLCD. Only 4 months old. I'll test the battery shortly and see how it lasts, thanks.
 

jgreco

Resident Grinch
Joined
May 29, 2011
Messages
18,680
Also be sure to check the firmware is current. I've seen strange error reporting with early version firmwares on various UPS's over the years.
 